3) Extended response time.

Up till now, the slave must respond within the allowed 256 ms. If it can't deal with the command, it could respond saying "busy". But that's not a good idea unless it's just a temporary situation, due to the slave doing some extended inner activity which cannot be interrupted. If a slave didn't reply at all, the master would probably do a retry (see 2 above) but you should not rely on this for satisfactory system operation - at the very least it throws out the scan timing.

I understand that HART rev. 6 will allow a properly-defined "delayed response" mechanism for use when a slave needs more time to reply properly. For field devices, it will only be allowed for "write" commands. For bridge devices running a higher communication speed to the master, it may apply to any command. The master remains responsible for making one or more further requests after a short time, to get the full reply.

Hope this helps a bit ...
Romilly.